Split load board
TNCS
30mARCD Tripping taking out all sockets, and boiler.
Tried to isolate problem by switching on MCB one by one to see which caused the problem.
Seemed to trip on multiple circuits
Stable with no load, but if a load connected on any circuit would trip intermittently.
Neutral Earth, was my thinking as its across different circuits.
IR reading did show 0.00 between N and E.
Circuit did work for a while though.
But if it was a reading of 0.00 how could it work at all.
I know that earth and neutral touching can trip the RCD as MCBs are single pole
The neutral of the circuit can still trip RCD if that MCB is off.
This is why it seemed like the fault was across multiple circuits ?
Is that correct.
Neutral Earth faults I am a bit unsure about.
Thanks
Ramp also showed a 21mA trip, Is that too sensitive, seems low to me.
TNCS
30mARCD Tripping taking out all sockets, and boiler.
Tried to isolate problem by switching on MCB one by one to see which caused the problem.
Seemed to trip on multiple circuits
Stable with no load, but if a load connected on any circuit would trip intermittently.
Neutral Earth, was my thinking as its across different circuits.
IR reading did show 0.00 between N and E.
Circuit did work for a while though.
But if it was a reading of 0.00 how could it work at all.
I know that earth and neutral touching can trip the RCD as MCBs are single pole
The neutral of the circuit can still trip RCD if that MCB is off.
This is why it seemed like the fault was across multiple circuits ?
Is that correct.
Neutral Earth faults I am a bit unsure about.
Thanks
Ramp also showed a 21mA trip, Is that too sensitive, seems low to me.