After diversity 18.4kW comes to 30A.
The future against which you want to 'proof' will hopefully be a future in which there is a more sensible approach to energy utilisation, not an increase in energy usage for the same tasks. In any event, unless people start cooking and eating a lot more than they do today, why should they ever need more energy for cooking than they do today?While 4mm maybe adequate for B32 everyone uses 6mm, and it seams a little silly to install smaller than average when you know you are having an induction hob and 2 ovens on the end. Not exactly future proof
Depends onAfter diversity 18.4kW comes to 30A.
Doubles or singles?ovens at around 5.5kw
After diversity 18.4kW comes to 30A.
Depends on
1) At what voltage the load is 18.4kW.
2) Which table in the OSG you look at.
Doubles or singles?
Most double ovens are around 5kW - are you really looking at having two double ovens? As in 4 cooking boxes.
Singles are typically 3kW or even less.
Imagine you were skilled at metal bashing, and you made a free-standing enclosure for the ovens and the hob, with a single electrical connection for them all. Would they use less power than if they were installed and supplied separately?Doesn't make sense to me to only apply 10A to all three loads. Common sense to me dictates applying 30A + 30% remaining.
You're right - provided that one pys adequate attention to 'what happens at the ends' (and that's not much of an issue with cooking appliances, there's never an (electrical) reason why one can't have a circuit with greater current-supplying capabilities than one needs. However, that does not mean that it is necessary, nor that one gains anything by doing it. ... but, if it makes you more comfortable, there no reason why you can't do as you wishI must admit I'm back to the idea of 45A circuit, I don't really see why not...looking at forums, doesn't seem so unusual to me.
Imagine you were skilled at metal bashing, and you made a free-standing enclosure for the ovens and the hob, with a single electrical connection for them all. Would they use less power than if they were installed and supplied separately?
Imagine if you bought a range cooker, with a hob and multiple ovens, and you had at it with angle grinders and hacksaws and separated out the hob and ovens, and installed and supplied them separately. Would they start to use more power than they did when combined into the cooker?
You're right - provided that one pys adequate attention to 'what happens at the ends' (and that's not much of an issue with cooking appliances, there's never an (electrical) reason why one can't have a circuit with greater current-supplying capabilities than one needs. However, that does not mean that it is necessary, nor that one gains anything by doing it. ... but, if it makes you more comfortable, there no reason why you can't do as you wish
As for "doesn't seem unusual', it would certainly not be unique - but I would say that it would be pretty "unusual" in terms of what is installed these days. In the past, all sorts of things were done, perhaps because people thought even less back then (if such is possible!) about what they were doing in those days, and did things "because other people did them". I inherited a particularly odd (unused) cooker circuit - wired in 10 mm² cable (Imperial equivalent) but protected by a 30A fuse - that did seem a bit daft!
Kind Regards, John
I would personally say that it's totally logical. As BAS has said, why on earth would several 'smaller' cooking appliances use less electricity if put together into one case, or one 'larger' cooking appliance use more electricity because it was split up into several different bits?I get that completely, but just because that's the outcome of the regs doesn't mean it's logical.
Don't forget that the diversity guideline we are talking about is the one for domestic installations - and the amount of cooking one does domestically will not differ according to how many or few #cases' one's cooking appliances are housed in. There are different guidelines in relation to commercial kitchens.Theoretically if you had infinite appliances the regs would be ridiculous, so at some number of applicances it becomes stupid...if you get what I mean.
It's not just BAS's logic - it's the same logic that most people apply.So I don't think blindly following your logic is a good idea.
Don't forget that what matters is 'average current for appreciable periods of time'. If absolutely everything were 'turned on full' from cold simultaneously (which is virtually never going to happen) then yes, the full 80A would initially be drawn, but only for a very short period of time. Even if you continued using every single bit of the cooking appliances, the thermostats would rapidly start turning things on and off, and you would soon reach the situation in which the average current over any appreciable period of time would be a small fraction of 80A.At 80A total load each would only have to be at 40% to max out the circuit. Am I the only one that thinks that doesn't sound so unlikely?
Well, you'd then be getting close to the 'usual' situation for a domestic cooker circuit - which I would say is probably 6 mm² cable (although 4 mm² would theoretically often be adequate) on a 32A MCB.I keep going back and forth (bearing in mind I won't be starting the install for weeks at least so no urgency!) but maybe I should hedge my bets in a similar fassion... 6 or 10mm depending on installation that could handle 45A and a 32A MCB. At least that way I wouldn't have to rip out all the plaster if 32A kept tripping. AFAIK there's no problem with that?
It's nothing to do with the regulations.I get that completely, but just because that's the outcome of the regs doesn't mean it's logical.
No - the more appliances the better.Theoretically if you had infinite appliances the regs would be ridiculous, so at some number of applicances it becomes stupid...if you get what I mean. So I don't think blindly following your logic is a good idea.
Then that must be how it works out.At 80A total load each would only have to be at 40% to max out the circuit.
Amongst those in the discussion - yes.Am I the only one that thinks that doesn't sound so unlikely?
I am talking about method C - clipped direct or buried in masonry.I keep going back and forth (bearing in mind I won't be starting the install for weeks at least so no urgency!) but maybe I should hedge my bets in a similar fassion... 6 or 10mm depending on installation that could handle 45A and a 32A MCB. At least that way I wouldn't have to rip out all the plaster if 32A kept tripping. AFAIK there's no problem with that?