It is possible that some debris may have become lodged in the isolating regulating valve.
To at least make sure this is ok turn the valve fully clockwise counting the the number of turns. Then fully anticlockwise fully anticlockwise then open clockwise the number of turns you counted.
The above needs to be done with system switched on .
This may solve the problem
The other problem maybe that this valve has been balanced too low to allow enough heat into the manifold. When the weather was warmer it would have worked ok but now there is a requirement for more heat output it needs to be adjusted open a little. (if you do decide to try this only open 1/2 a turn extra as too much will cause other balancing problems
my apologies to the op, I reckon the confusion was all mine, if you take the head off the injector valve the ufh will run at max temp not min as I suggested , if its running at 30c with the head off then its in all probability the valve rather than the head or sensor.