Looking at your kitchen floor plan, it seems evident that the water flow goes to the right hand side of your kitchen before going to the utility. Warm on that side of the kitchen but cold in the utility indicates a poor flowrate to the kitchen circuit. If you are convinced that the other d/s rooms are heating normally then I suggest taking action in the following order:-
1. Take the kitchen actuator head off its mounting, and check the pin for full movement. Compare it against that of a working circuit's pin. if the floor diagram is true then I suspect the kitchen circuit will be the right hand end of the manifold, ie furthest from the pump.
2. Check and clean the pump impellor, just a small amount of debris in here can reduce pump performance (and balance) significantly, increasing pump vibration too.
3. Disconnect the kitchen circuit and flush the pipes with clean water to remove suspended debris. You can isolate the individual circuit by turning the slot you described to horizontal, then replacing the electrical actuator with a screw-down manual cap. When finished open the individual isolators one at a time to flush debris from the manifold into a bucket.
Turning attention to the pump running-on problem, it could be that the electrical system demands the pump to continue running after the demand has been satisfied, either for a set period of time or until return temperature drops below a set figure, say 40C. That's a question for the controller manufacturer/agent.
Hope this helps.
1. Take the kitchen actuator head off its mounting, and check the pin for full movement. Compare it against that of a working circuit's pin. if the floor diagram is true then I suspect the kitchen circuit will be the right hand end of the manifold, ie furthest from the pump.
2. Check and clean the pump impellor, just a small amount of debris in here can reduce pump performance (and balance) significantly, increasing pump vibration too.
3. Disconnect the kitchen circuit and flush the pipes with clean water to remove suspended debris. You can isolate the individual circuit by turning the slot you described to horizontal, then replacing the electrical actuator with a screw-down manual cap. When finished open the individual isolators one at a time to flush debris from the manifold into a bucket.
Turning attention to the pump running-on problem, it could be that the electrical system demands the pump to continue running after the demand has been satisfied, either for a set period of time or until return temperature drops below a set figure, say 40C. That's a question for the controller manufacturer/agent.
Hope this helps.