What about getting hold of a suitable isolating transformer to power the heating from, and see what happens?
That is the way to measure it.
Use a high impedance meter measuring volts located next to the earth reference point and a long lead to the test pad will show the induced voltage. The voltage should reduce if a resistive load connected between the test pad and earth.
If you want a thorough test result then move the pad until you find the locations with highest voltages per mat and use those as the test sites.
Note the voltage without a load across the meter. Then connect a load across the metter and adjust the resistive value of the load across the meter until the voltage drops to be half the un-loaded voltage. Then the resistive load is approximately equal to the impedance of the capacitive coupling between heating mat and the area of the test pad. From that you can then work out if the capacitive coupling is sufficient to permit a dangerous amount of energy to be capacitively coupled into a body that is in contact with an earth or other route for that energy to pass through the body to cause injury.
What about getting hold of a suitable isolating transformer to power the heating from, and see what happens?
The induced voltage from the floor (if that is what the problem is) is powered from a source that has its reference at earth (the supply substation).
If you put in an isolating transformer then you separate the earth reference to the UFH and the supply is then floating (the same as a shaver socket in a bathroom).
The theory is then that there could be no potential between the floor (floating supply) and anything else that has earth at its supply.
If this were to solve the problem, where would that leave us with regard to the RCD protection stipulated by the regs? Presumably placing the RCD on the load side of the isolating transformer would be in compliance?
If this were to solve the problem, where would that leave us with regard to the RCD protection stipulated by the regs? Presumably placing the RCD on the load side of the isolating transformer would be in compliance?
What use would it be? The supply to the UFH would be electrically separate from mother earth. That's not to say you can't have an earth connection on the secondary side of an isolation transformer in order to use an RCD, but you still need to connect the earth to something for it to be of any use. As you don't have an earthed grid or UFH cable with integrated screen, that doesn't leave you with a lot of options.
I am still very keen to try this experiment for measuring the induced voltage. Any recommendations on the best/most cost effective means of placing a reliable, easily adjustable resistance across the meter?
Any comments on my thoughts about the grout being the path to earth?
Would I be right in assuming that in the absence of RCD protection, electrical separation provides sufficient fault protection in order to comply with the regs? This is my understanding but to have it confirmed or otherwise would be very much appreciated.