hi guys
i have been asked to add on an fcu via spur to a ring as usual. however when inspecting, i have seen that this ring has been wired in 4mm2 cable, and consequently there is not much room in the socket terminations to add on another set of 4mm conductors (not even 2.5mm. ps this is definitely a ring!)
im not entirely sure, but i think i recall reading somewhere, that all reductions in cable size can be fused within 3m of the reduction in cable size. is this correct?? if so, where is it stated? (as i have to be sure). i assume that this would then permit the attached diagram to be connected..
http://i7.photobucket.com/albums/y278/user56565/fcu.jpg
im not sure if there's a safety issue in this. short circuits due to a mis-drill etc on the 'unfused' part of cable would be easily handled without any cable damage by a type B. overload on this part of the cable wouldn't be possible because of the FCU. ps the 'unfused' cable is very short in length (10cm or so).
i apologise for asking. i have never come across a ring wired thicker than 2.5, and thus haven't been in this situation ever before. rather than get things messy trying to do it the typical way (maybe changing sockets, using junction boxes etc), i thought i should check on this first as im sure ive read this somewhere before.
many thanks
i have been asked to add on an fcu via spur to a ring as usual. however when inspecting, i have seen that this ring has been wired in 4mm2 cable, and consequently there is not much room in the socket terminations to add on another set of 4mm conductors (not even 2.5mm. ps this is definitely a ring!)
im not entirely sure, but i think i recall reading somewhere, that all reductions in cable size can be fused within 3m of the reduction in cable size. is this correct?? if so, where is it stated? (as i have to be sure). i assume that this would then permit the attached diagram to be connected..
http://i7.photobucket.com/albums/y278/user56565/fcu.jpg
im not sure if there's a safety issue in this. short circuits due to a mis-drill etc on the 'unfused' part of cable would be easily handled without any cable damage by a type B. overload on this part of the cable wouldn't be possible because of the FCU. ps the 'unfused' cable is very short in length (10cm or so).
i apologise for asking. i have never come across a ring wired thicker than 2.5, and thus haven't been in this situation ever before. rather than get things messy trying to do it the typical way (maybe changing sockets, using junction boxes etc), i thought i should check on this first as im sure ive read this somewhere before.
many thanks