We are all familiar with the fact that, in the context of an RFC wired entirely with 2.5mm² cable, Appendix 15 ("Informative") of the regs indicates that an unfused spur should feed only one socket, whereas a spur connected via an FCU (fuse 13A) can feed an unlimited number of sockets.
I presume that this recommendation relates essentially to the current-carrying capacity of the cable - both within the spur circuit and also in the ring itself (since an extensive spur connected close to one end of the ring could result in most of the current going through one 'leg' of the ring - just as if many heavily-loaded sockets were installed close to one end of the ring).
If that is the case, then I think I could produce a fairly compelling argment for it to be acceptable to have an unfused spur with several sockets if it were wired in 4mm² cable, particularly if it were connected roughly at the mid-point of a ring. With such an arrangement, no cable would carry any more current than in the 'recommended' designs for RFCs or radial circuits. The wiring of the spur circuit itself would certainly be no problem since, with 4mm² cable, it would be identical to what is recommended for an unfused spur to a 4mm² radial final. As for the ring itself, the situation would be no worse than having several sockets close to each other on the ring at the point at which the spur was to be attached.
An advantage of such an arrangement would be that it could often result in an appreciable reduction in the total length of the ring (where most of the load would probably be), not to mention various possible practical installation advantages.
Any thoughts, or arguments against what I have suggested?