433.3.1(ii)BAS, i have no idea why?
Who is installing the circuit? If you are hiring an electrician he will be better positioned than us to confirm what you have and can have.
Alison, remembering your other posts, doesn't your mother live in a council / HA flat? Are you allowed to do this sort of work in the property?
Are you sure that it is a good idea to say things when you have no idea?BAS, i have no idea why?
I know you were, as unlike you I am able to pay attention.As i was referring to Flameport's post
The cable is 6mm. There are no sizes between 6 and 10mm, so if it is smaller than the 10mm piece, it is 6.Ive no problem about replacing the MCB for a 50amp but it's the cable that I'm concerned about.
You can't use a 50A MCB, as that is greater than the cable rating, which is 47A assuming it is not contained in insulation or conduit.
A 45A MCB could be used, if one can be obtained for your consumer unit.
A 10.5kW 240V shower is 43.75A.
Listen to this man
DS
For what reason(s)?No, i would not install a 50a breaker on a 6mm cable.
Indeed. It's also untrue that it would operate at 45A in 16 minutes, as it mustn't operate at a current of less than 1.13 times its rating (which is 45.2A), but must operate within an hour at 1.45 times its rating.No, it won't.a 40A type B MCB will allow 45A through it for around 16 minutes before it will trip, so that will probably be OK
Ib ≤ In ≤ Iz
[EDIT]Formatting changed to focus on the relevant part of the rule[/EDIT]
Not sure how many times I have said this:No, i would not install a 50a breaker on a 6mm cable. Minimum cable size i install for showers is 10mm.
Kindest regards,
DS
But you will remain incapable of understanding it?You can keep on saying it.
DS