Yo. Wilts - there's plenty of new stuff to help with - no point wasting your time replying to a passing visitor who hasn't been back since mid-March...securespark said:Wilts
Why the interest in a thread from 7 months ago?
Yo. Wilts - there's plenty of new stuff to help with - no point wasting your time replying to a passing visitor who hasn't been back since mid-March...securespark said:Wilts
Why the interest in a thread from 7 months ago?
Yup - but you could turn them all on at once - your description applies to how they behave once they are at the working temperature you want, but during warm-up, which could be quite long if there are pans etc to heat up, not just rings etc, you will see the full load current.Damocles said:It is quite normal to assume that not all elements of a cooker will be operating at full power at once. In fact this is very unlikely, if you consider that they work by switching the heating elements on and off every now and then.
Fine to use that diversity calculation when assessing the total demand, but risky down at the individual circuit level...Cooker diversity rules are 10A plus 1/3 of remaining theoretical load. Taking the two devices separately this gives 10+10+ 1/3(30)=30A
So a 30A would likely do, never mind 40. Calculations like this are a bit rule of thumb. It is not obvious why separate hob and oven units should be treated any different from an all in one cooker. In that case it would be 10+ 1/3(40)=23A.
You are not supposed to rely on the protective device to prevent overloads
Me too.Damocles said:Well, there are two schools of thought on the applicability of the rule. I would not be surprised to find that most cooker supplies rely upon diversity rather than maximum load.
Me neither. Got gas anyway, and when replaced the plan is for a gas hob & electric oven, but whatever, my habits would remain the same. And I always use the kettle if I want a pan of boiling water - more efficient. But it's not mega-rare for me to have 3 or 4 rings and the oven on the go - OK, not flat out, but who's to say for how long they would be if, unlike a gas hob, you need to wait for them to get hot? Finally, let's not forget self-cleaning ovens, which run very hot (I suspect flat out) for a substantial time.As to whether you might turn on everything at once, that would mean putting on four saucepans of cold water and both ovens at exactly the same time. How often do you do that? I never have.
Socket circuits are different from ones designed to supply 1 or 2 fixed items.You are not supposed to rely on the protective device to prevent overloads
Well, how on earth do socket rings work then? What happens if you plug in ten electric fires at once? It is assumed that you will not do this, but if you do the MCB/fuse will disconnect before any harm is done.
Yup - and if that 10 minutes happens 3 times a day for 25 years, what does it do to the cable? What I meant by the above is that you are not supposed to rely on the protective device to limit the load. It, and the cable, should be sized to allow the design current, and it should be rated so that it will protect the cable if something goes wrong, but that's it. Ib <= In <= Iz. If ever you find yourself saying (at the circuit level) "it doesn't matter if everything is turned on at once because the MCB will trip" then you've got a bad design.Cabling IS designed to work with protective devices. It is expected to get warm in use, and to to work satisfactorily and safely in the event of small overloads, up to the point at which the mcb trips. A 40A mcb may work happily at 50A for 10 minutes.