Using oven supply for double socket

Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.

How far will the sockets be from the cooker outlet?
 
Sponsored Links
Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.

How far from the sockets be from the cooker outlet?

No dishwasher now, just washing machine and lights for gas cooker.Cooker outlet is gone, I'm using the cable for a double socket.
 
Yes thanks,but my query is what fuse rating do I use at the fuseboard to replace the one removed and lost by the builder?
 
Sponsored Links
Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.
Indeed - but the OP should be aware that if he is going to 'daisy chain' two (or more) sockets on a radial, he'll have to use at least 4mm² cable for the connection between the sockets (and, indeed, the connection to the first socket, if the cable is joined, rather than taking the existing 6mm² one all the way to the socket) if the circuit is being protected by a 30A fuse.

Kind Regards, John
 
Indeed - but the OP should be aware that if he is going to 'daisy chain' two (or more) sockets on a radial, he'll have to use at least 4mm² cable for the connection between the sockets (and, indeed, the connection to the first socket, if the cable is joined, rather than taking the existing 6mm² one all the way to the socket) if the circuit is being protected by a 30A fuse.
That's why I asked about the distance but as he is only going to fit one double socket it doesn't apply.
 
Indeed - but the OP should be aware that if he is going to 'daisy chain' two (or more) sockets on a radial, he'll have to use at least 4mm² cable for the connection between the sockets (and, indeed, the connection to the first socket, if the cable is joined, rather than taking the existing 6mm² one all the way to the socket) if the circuit is being protected by a 30A fuse.
That's why I asked about the distance but as he is only going to fit one double socket it doesn't apply.
Fair enough. I guess it depends who he takes most notice of - he was previously advised to fit two single sockets, rather than a double.

Kind Regards, John
 
Fair enough. I guess it depends who he takes most notice of - he was previously advised to fit two single sockets, rather than a double.
Yes, that's what I thought and (also) why I asked about the distance but apparently the dish-washer has turned into a gas hob.
 
Fair enough. I guess it depends who he takes most notice of - he was previously advised to fit two single sockets, rather than a double.
Yes, that's what I thought and (also) why I asked about the distance but apparently the dish-washer has turned into a gas hob.
Maybe. We obviously interpreted it differently. I took "No dishwasher now" to mean 'not yet' (i.e. to be added later) - but you seem to have taken it to mean 'new plan - no dishwasher ever, just gas hob'.

Kind Regards, John
 
Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.

How far will the sockets be from the cooker outlet?

No dishwasher now, just washing machine and lights for gas cooker.Cooker outlet is gone, I'm using the cable for a double socket.
Can only go on information given.
 
Just to confirm, I've fitted a double socket which will only be supplying a washing machine and light for the gas cooker. We now have no space for a dishwasher. It's 6mm2 cable approx 8 metres back to fuseboard with 30 amp fuse fitted. trust that's ok.
Many thanks to you all!
 