Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.
How far will the sockets be from the cooker outlet?
How far will the sockets be from the cooker outlet?
Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.
How far from the sockets be from the cooker outlet?
Indeed - but the OP should be aware that if he is going to 'daisy chain' two (or more) sockets on a radial, he'll have to use at least 4mm² cable for the connection between the sockets (and, indeed, the connection to the first socket, if the cable is joined, rather than taking the existing 6mm² one all the way to the socket) if the circuit is being protected by a 30A fuse.Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.
That's why I asked about the distance but as he is only going to fit one double socket it doesn't apply.Indeed - but the OP should be aware that if he is going to 'daisy chain' two (or more) sockets on a radial, he'll have to use at least 4mm² cable for the connection between the sockets (and, indeed, the connection to the first socket, if the cable is joined, rather than taking the existing 6mm² one all the way to the socket) if the circuit is being protected by a 30A fuse.
30A will be alright.Yes thanks,but my query is what fuse rating do I use at the fuseboard to replace the one removed and lost by the builder?
Fair enough. I guess it depends who he takes most notice of - he was previously advised to fit two single sockets, rather than a double.That's why I asked about the distance but as he is only going to fit one double socket it doesn't apply.Indeed - but the OP should be aware that if he is going to 'daisy chain' two (or more) sockets on a radial, he'll have to use at least 4mm² cable for the connection between the sockets (and, indeed, the connection to the first socket, if the cable is joined, rather than taking the existing 6mm² one all the way to the socket) if the circuit is being protected by a 30A fuse.
Yes, that's what I thought and (also) why I asked about the distance but apparently the dish-washer has turned into a gas hob.Fair enough. I guess it depends who he takes most notice of - he was previously advised to fit two single sockets, rather than a double.
Maybe. We obviously interpreted it differently. I took "No dishwasher now" to mean 'not yet' (i.e. to be added later) - but you seem to have taken it to mean 'new plan - no dishwasher ever, just gas hob'.Yes, that's what I thought and (also) why I asked about the distance but apparently the dish-washer has turned into a gas hob.Fair enough. I guess it depends who he takes most notice of - he was previously advised to fit two single sockets, rather than a double.
Can only go on information given.Oh sorry, well fit the 30A otherwise you will likely not be able to us WM and DW at the same time.
How far will the sockets be from the cooker outlet?
No dishwasher now, just washing machine and lights for gas cooker.Cooker outlet is gone, I'm using the cable for a double socket.
Fair enough - I didn't notice the "double socket" bitCan only go on information given.No dishwasher now, just washing machine and lights for gas cooker. Cooker outlet is gone, I'm using the cable for a double socket.