Vaillant 824 bypass valve

Joined
27 Sep 2010
Messages
1,271
Reaction score
243
Country
United Kingdom
Hi,
I have installed underfloor heating with 22mm pipe from boiler to the manifold. There are two honeywell 2 way valves on the UFH and radiator returns for control.

When either UFH or radiators call for heat the boiler starts and then gives up. I think it goes in to anti cycle mode? Flame symbol is not lit and d.67 (remaining burner anti cycle timer) starts to count down from 5 mins. When at 0 the flame symbol lights and the boiler heats again...

When I watch d41 (return temp) it shoots up. The return to the boiler from rads/UFH is cold.

Is this likely to be an internal bypass issue?

Why would this start to happen now? Are the honeywell valves really restricting?

What would be my next steps? Am I right in thinking I should not remove the front cover?

Thanks....
 
Last edited:
Sponsored Links
As far as I know it has worked OK previously. Not really paid too much attention to it. The house did always heat up quickly so fairly sure the boiler was not cycling like it is now.

The zone valves must open as the UFH and rads will get hot... Im guessing there is no way to tell if they are fully opening?

Has it ever worked?Are any valves closed are the zone valves powering open
 
Any work carried out at the boiler or system recently?
 
Sponsored Links
Only me draining the system and soldering in UFH pipework and valves. Nothing boiler related...

I wonder if something is lodged in the bypass causing it to stick open?

Any work carried out at the boiler recently?
 
If it were the bypass, then the boiler return would be hot underneath. I’m thinking that there’s a valve closed off somewhere too. I was thinking at the boiler, hence me asking.
 
The bypass is built in to the boiler - I think it bypasses without using the flow and return under the boiler?

If it were the bypass, then the boiler return would be hot underneath. I’m thinking that there’s a valve closed off somewhere too. I was thinking at the boiler, hence me asking.
 
Thanks all for the replies.

I have cleaned out all filters etc which has helped.

Now when the radiators are running the boiler is fine. The temp on d.41 (return temp) is as expected.

When running the UFH d.41 shoots up! It must be bypassing. Are UFH manifolds very restricting? Could it be faulty? Or do I need a valve on that loop to provide less resistance so it doesn't bypass? Maybe a lever valve next to the manifold that's just cracked open...

Might put a call in to polypipe Monday to see if they have any suggestions....
 
Can you post some clear pictures of motorised valves and pipework to underfloor/boiler. If I read your first post correctly the zone valves are on the return? That's not normal method!
I'm a polypipe underfloor contractor so may be able to give you some pointers.
 
I checked the manuals and only the 3 way valves state not to install it on the return. Apparently it doesn't matter with the two ports? The radiators are working fine. Just appears the UFH manifold is very restricting and causing the boiler to bypass and then cycle.

How accurate should the blending valve be? Mine seems to jump about a fair bit. The input temp is jumping from 40 to 60 degrees but the output temp from the blending valve doesn't seem consistent?

I didn't get any real instructions with the manifold so I probably don't have it setup correctly at all!

I will post some pictures in a bit...

Can you help with the basic manifold settings?
I have two loops 63 and 66m. What settings should I use for the flow adjustment and pump speed (I,II, Rad or UFH)

What flow rate should I be getting on the gauges? They are only marked Min and Max...

Cheers...

Can you post some clear pictures of motorised valves and pipework to underfloor/boiler. If I read your first post correctly the zone valves are on the return? That's not normal method!
I'm a polypipe underfloor contractor so may be able to give you some pointers.
 
AAD6B619-A72C-47F7-96EE-62E84F1A84FD.jpeg
 
D0BE76F3-B7E1-44C8-A1EF-C4764D48336A.jpeg
 

Attachments

  • A1851463-107F-40C4-9F58-F4D6E05B31FD.jpeg
    A1851463-107F-40C4-9F58-F4D6E05B31FD.jpeg
    290.3 KB · Views: 75
Hi, they are free moving. The caps are lightly screwed on and not pushing the pins down.
When I turn the pump to II the flow shows near max with the flow restrictor set to 30

The 2 blue caps remove them and make sure actuator pins are moving freely.
 