Several times in a week, system flow water temp settles at mid 50s (return: high 40s) when the set flow temp is 75.
Room stats calling for heat, burner on, pump on, pressure OK, no new codes. Just doesn't rise to the set flow temp. This continues until boiler is switched off, cools down (to mid 30s), and when it restarts sometimes it's all fine and runs at flow 75 (return: high 60s) and sometimes settles back to flow mid 50s again. Can't predict.
5-bed house, HW cyl, DHW to kitchen, underfloor heating in extension - and on a good day even when v cold outside runs fine all day at 75 with everything calling for heat - house comfy. On a bad day, mid 50s again - need extra jumpers.
Any ideas...?
It's as if it's modulating too far down and then not noticing the gap between flow temp and set temp....sometimes.
I've tried....
- Turn set temps (CH & DHW) down and back up again; no effect.
- Switch boiler off and on again; no effect.
- Boiler reset; no effect
- Switch each heat demand off and on again; no effect.
- Set thermostats higher; no effect
- Turn set temp down, waited for water to cool significantly, set temp up again. Sometimes this fixes it, sometimes not.
Room stats calling for heat, burner on, pump on, pressure OK, no new codes. Just doesn't rise to the set flow temp. This continues until boiler is switched off, cools down (to mid 30s), and when it restarts sometimes it's all fine and runs at flow 75 (return: high 60s) and sometimes settles back to flow mid 50s again. Can't predict.
5-bed house, HW cyl, DHW to kitchen, underfloor heating in extension - and on a good day even when v cold outside runs fine all day at 75 with everything calling for heat - house comfy. On a bad day, mid 50s again - need extra jumpers.
Any ideas...?
It's as if it's modulating too far down and then not noticing the gap between flow temp and set temp....sometimes.
I've tried....
- Turn set temps (CH & DHW) down and back up again; no effect.
- Switch boiler off and on again; no effect.
- Boiler reset; no effect
- Switch each heat demand off and on again; no effect.
- Set thermostats higher; no effect
- Turn set temp down, waited for water to cool significantly, set temp up again. Sometimes this fixes it, sometimes not.