I had a problem this morning with this boiler,when I arrived on site it was showing fault code f20 which is overheat.I checked the fault list in the menu and this has not happened before.The boiler lit after resetting it and ran ok,I checked the meter readings off the flow and return thermistors and the readings were correct,1.2k ohms at around 40 degrees.Everything warmed up through the building so I dont suspect the pump and dhw was fine too.The boiler came right up to max temp and shut off on the boiler stat,I let it cut in and out a few times and all was ok,or so I thought.When I turned the boiler off on the switch on the boiler fascia and turned it back on a minute later it went straight to f20 again,I reset it and it lit ok.I tried turning it off and on via the external programmer and it was fine every time,it only goes to f20 if I turn it off on the boiler switch on the fascia,on one occasion it showed f25 which is low system pressure,then went to f20,the system pressure is 1.5 bar.Has anyone else come across this scenario ?,I suspect the pcb and have one on order,but it would be nice to have some other thoughts,thanks.