I've recently noticed a problem with my CH. The sytem is as follows:
1. Owl Intuition control system.
2. Two Myson MPE222 zone valves, one for CH and one for HW
3. Grunfoss pump.
4. Vaillant Ecomax Pro boiler.
The boiler, pump and zone valves are all about 10 or 11 years old.
The Owl Intuition boxes actuate the zone valves and the auxiliary switches in the zone valves turn on boiler demand. The pump is controlled by the boiler.
Sometimes during a heating cycle the following happens:
1. Thermostat cuts in
2. Zone valve actuates
3. Boiler starts.So far so good.
4. At some point before the thermostat setpoint is reached, typically just as the boiler is reaching its max temp set point, the boiler switches off. When this happens there is no error recorded on the boiler. The light on the zone valve is still illuminated, the valve is still open and the pump is still running. If sufficient time passes before the boiler restarts, then the pump shuts down, presumably at the end of overrun. At some point, the boiler starts up again and normally the demand cycle is completed.
My thoughts are that it's either a fault on the boiler or a fault in the zone valve. Since no error is recorded or displayed on the boiler, I'm inclined to point the finger at the zone valve microswitch.
It's a bit tricky to narrow down as it's not a hard fault. I'm going to try to measure the AC on the switched output from the zone valve tomorrow if I can catch it playing up, but in the meantime, what's the general consensus?
Thanks in advance for your thoughts.
1. Owl Intuition control system.
2. Two Myson MPE222 zone valves, one for CH and one for HW
3. Grunfoss pump.
4. Vaillant Ecomax Pro boiler.
The boiler, pump and zone valves are all about 10 or 11 years old.
The Owl Intuition boxes actuate the zone valves and the auxiliary switches in the zone valves turn on boiler demand. The pump is controlled by the boiler.
Sometimes during a heating cycle the following happens:
1. Thermostat cuts in
2. Zone valve actuates
3. Boiler starts.So far so good.
4. At some point before the thermostat setpoint is reached, typically just as the boiler is reaching its max temp set point, the boiler switches off. When this happens there is no error recorded on the boiler. The light on the zone valve is still illuminated, the valve is still open and the pump is still running. If sufficient time passes before the boiler restarts, then the pump shuts down, presumably at the end of overrun. At some point, the boiler starts up again and normally the demand cycle is completed.
My thoughts are that it's either a fault on the boiler or a fault in the zone valve. Since no error is recorded or displayed on the boiler, I'm inclined to point the finger at the zone valve microswitch.
It's a bit tricky to narrow down as it's not a hard fault. I'm going to try to measure the AC on the switched output from the zone valve tomorrow if I can catch it playing up, but in the meantime, what's the general consensus?
Thanks in advance for your thoughts.