Help required with the wiring of a Vaillant ecotec 418 Boiler.
No 4 terminal on the PCB: should this be voltage free ie the switched live for the boiler, as this terminal has a negative feed when checked with a meter.
can anyone help with this problem

Thanks in anticiption
 
Sponsored Links
Thanks for the reply, however when connecting the switched live to the No 4 terminal, the House rcd tripped. Checked No 4 terminal and found that when meter connected to Line +Pos (Boiler) and No 4, meter read 230 Volts, therefore it appears that the No 4 terminal is getting a Negative feed through the pcb.
Again any help would be appreciated.
 
Have you removed the link between 3 and 4 ?? The link must be removed before any external controls are wired into the boiler. These boilers are either volt free through a volt free switched clock or room stat using both 3 and 4 as the switch circuit or by wiring the switched live output from the external controls straight into 4 (1 live wire, no neutral). If you are tripping the rcd there is some problem with your wiring. Switched live comes from whatever version of zone valving you have.
 
Sponsored Links
Again thanks for the reply, the Pos live switched feed is from the zone controls, however the No4 terminal has a negative feed through the pcb. Therefore when the switched feed is connected to No4 there is a dead short and the rcd trips.

Any help appreciated.
 
Just checked and 4 is definitely the right terminal for a 240v feed from external controls with link removed. remove the switched live wiring from 4 and switch boiler power on, test terminal 4 for 240v , it should have nothing if tested with a neutral or earth on the other meter probe. If it has 240v there is a fault with the pcb, if it still trips the rcd you have an external wiring fault
 
Remove your wire to terminal 4, then re-instate the link between 3 and 4.

If your RCD/trip still blows then there appears to be a fault on the board. If not it is a fault in the external controls.

What about the pump? This is controlled by the pcb. Try removing this from the equation, or testing with your multimeter ;)
 
Do what dave suggests first but What external contols do you have is it 2 two port valves or a mid position. pump should be wired back to boiler terminal position for all installs.
 
You will get 230v dropped across 3 and 4.

For reasons which are obvious.

If you are tripping out an RCD you do not have a short between L and N.

You have an earth leak somewhere.

Whilst it is probably an external wiring fault, we had an early 4 series with strands of metal swarf in the PCB enclosure, which caused a similar problem.

The 'British Vaillant' syndrome....
 
Thanks for the info. Simond right, problem was an earth fault on the switched live.
A small nib of wire protruding from a row of Choc boxes earthing onto the metal patress box. Problem solved.

Thanks to all who wrote in.

Cheers Ray
 