Thanks. In case it's a faulty wire connection, I'm going to check that out the voltage on T4 is actually 240V with a meter, and try the link between T3-T4 to confirm the fault is still there. I'll probably go the replace pcb route.If the boiler is showing S.30 with 240VAC on T4, odds on its a new PCB. Double check at D.8, 0 is no signal recognised from external controls, 1 signal recognised from external controls. Expect 0 in your case. Double check the wire to T4 is tight and test to the Neutral terminal or T5 on the PCB. A board replacement is not out of the way at 10+ years. They are susceptible to power supply rail issues the older they get with capacitors failing, so don’t feel too hard done by. Setting up and combustion checks with a FGA need to be carried out by a GasSafe engineer when fitting a new PCB.