Looks that way, installing a isolating valve should narrow down (if) the problem.This is odd. The DHW at boiler is hot to touch, i.e. the 43 degrees D.04 reading being given is correct. If I grip the pipe it becomes uncomfortable after 5-7 secs.
However, 2.5m away, at the kitchen HW tap, the water’s lukewarm!
There’s a tee beneath the boiler leading to a WC, and closer to the sink, another tee to the bathroom. I’ve closed the WC basin’s HW isolator (it’s a mixer tap). This doesn’t make any difference to the temp of water from kitchen tap.
I’d isolate the mains CW at the kitchen tap but unfortunately there’s no isolator fitted. I’ll fit one later today - however, given above strongly suggests there is a fault with the kitchen mixer tap?
9LPM @ 42C + 7LPM @ 19C = 16LPM @ 31.9C.Also, faulty mixer tap in kitchen would explain why the D.36 readings don’t reflect the actual flow rates I’m measuring at the kitchen tap (8.5 LPM, D.04 is 4) or bath tap (16 LPM, D.0.04 is 9)?
The boiler shouldn't even fire up in DHW mode if the mains into it is actually isolated. If it doesn't fire up and there is still "HW" flowing from any tap then definitely a mixer problem.Lastly, probably a separate issue. I notice if I isolate mains CW immediately beneath the combi, with a quarter turn using an Allen key, it doesn’t work. DHW at kitchen sink continues to flow.