gas4you said:
I know all there is to know about Vaillants, well the new ones, as I live and breathe them
You should know then.
But whatever anyone replies to you on here you will google and find a diversve reason to tell them that they are wrong.
So, as i am not prepared to descend into another pointless post/argument with you I feel there is no point in wasting my time with an intelligent response, apart from this one.
If you know how this combi operates then please tell us all. The manual does not explain in any detail the operation.
What temp' is the water stored at?
How does it blend down the temp - if it does blend down?
etc?
You are a Vaillant expert, not me. I am an engineer who understands drawings and the likes and understands descriptions too. Just explain how it works to magically get 15.5 litres/min into 20 litres/min by adding a 15 litre tank on the back.
Just musings from me:
Most combis do not condense when producing DHW. The return from the plate back to the main heat X is kept high (lowering DHW flowrate) to ensure the delta T of the main heat X is kept within temperature spec. They also skimp with the plate heat Xs, not extracting enough heat from the boilers main heat X (they want t keep the plates small to save space too).
They can fit a larger plate heat X. Feel the 100 kW plate heat X on a heat bank and the returning water to the store is "cool", very cool, far cooler than what is on combis. Vaillant by using the tank ensure that the returned water to the plate is "cool" as the cold mains enters at the tanks bottom and this is pumped immediately back to the plate heat X. That adds efficiency and raises the flowrate. How much I don't know, or whether the rise is significant.
If the mains water tmep is 5C, tye return temp to the plate heat X maybe 7C (mixing in th tank). Raises the temp 35C to 42C. This is pumped to the top of the tank (too cold for the outlet). This may mix with the hotter water in the tank blending up.
There is flow guage that tells the pcb the cold mains pcb flow. The bottom of the tank temp is known, as is the temp from the plate to the tank. "IF" the tank pump modulates then the temp of the water going to the tank can be controlled. "IF" the water in the tank is stored at "n" temp, then the temp of the water to the tank can be controlled as they know what temp it should be to get the correct outlet blend temp. There is no temp sensor on the DHW outlet which I find odd.