Vaillant F75 pressure sensor errors

Joined
8 Mar 2014
Messages
25
Reaction score
7
Location
Worcestershire
Country
United Kingdom
Pressure sensor needs replacement again after three F75 faults in a month. All cleared by using the ignition button but I’m getting to the stage where I may be simply replacing my pre-2010 Ecotec. A poor 10 year history of reliability - four pressure sensors, a heat exchanger, o rings and diverted valves. I’m on first name terms with the engineer . I understand newer Vaillants are more reliable but my experience with the Ecotec had put me off. Worcester Bosch?
 
Sponsored Links
Are you sure it’s the pressure sensor? IME if it’s the sensor, then it’s down to a dirty system. We have literally hundreds of these boilers on our patch in social housing, some have the sensor replaced often, others have had the original orange one. Whenever I changed one I look to see how blocked it is, and they’re usually full. You can’t go blaming the boiler for doing it’s job if the system is dirty.
 