The very nice picture of the pipework is not a low loss header arrangement as used/recommended by keston boilers. Give there tech dept a call and they will fax/mail you a drawing of there idea/method for a low loss header.
It is not a low loss header, it is just a flow and return header system, this is a low loss header
http://i171.photobucket.com/albums/u292/silverback_2007/DSC00884.jpg
Cheers, thats how we used to do them or should I say our welder did.
My then boss used to spec them up.
What did you do for design/sizes? of the vertical diameter?
Add up the cross sectional area of all F & R's and allow a bit?
or am I over simplifying it.
It is not a low loss header, it is just a flow and return header system, this is a low loss header
http://i171.photobucket.com/albums/u292/silverback_2007/DSC00884.jpg
This has about as much resemblance to a low loss header as Diyitall's first image.![]()
I was surprised they didn't stagger the the primary side billybob
what else would you call it
billy bob wrote
what else would you call it
A hydraulic decoupler.![]()
Consisting of four connections (as your image shows) which allows the heating load to be distributed over several boilers giving higher operating efficiencies allowing some boilers to be switched off at part load operation.
Yes, as in the case of the low loss header it has negligible pressure drop over its length.
However with the low loss header or low pressure header system multiple secondary circuits can be connected directly to the header pipe with each secondary circuit requiring its own secondary circulation pump.