it definetly points to two causes of your pressure rise
faulty expansion vessel or holed plate exchanger
note that your location is glasgow, not saying we never get holed plate exchangers,but its something i find very rarely.
to rule out a holed plate exchanger, isolate the 15mm cold inlet underneath boiler on right hand side,de pressurise to 1.3bar and run on ch
if pressure rises and starts running out PRV,then expansion vessel/expansion vsessel hose is defective.
manual will tell you how to replace it, quite a straight forward job
post back with results
faulty expansion vessel or holed plate exchanger
note that your location is glasgow, not saying we never get holed plate exchangers,but its something i find very rarely.
to rule out a holed plate exchanger, isolate the 15mm cold inlet underneath boiler on right hand side,de pressurise to 1.3bar and run on ch
if pressure rises and starts running out PRV,then expansion vessel/expansion vsessel hose is defective.
manual will tell you how to replace it, quite a straight forward job
post back with results