The pressure in my Vokera Linea 24 keeps on rising.
If I open a Hot tap, the pressure drops , but the water comes out of the tap dirty. On closing the Hot Tap the pressure begins to rise again, reaching over 3 bar.
The only way to stop the pressure rising is by closing the cold water feed to the boiler, which means I have no hot (dirty) water, but I do have central heating.
After seeking advice I have removed, checked and replaced the loop filler valve to make sure it is not "passing" I have fitted an overhaul kit to the diverter valve, also I have replaced the safety valve.
What do you think should be my next step.
Cheers. Dek.