vokera maxim

Joined
25 Jan 2007
Messages
289
Reaction score
34
Location
Yorkshire
Country
United Kingdom
hot water works fine, had two pumps fitted in the last 5 years, when on heating only, boiler fires for about 5 mins, then cuts off (not reset, just reaches temp), and then fires every 2/3 mins for about 30 secs, all rads are just luke warm, but flow pipe out of boiler is red hot, return is not even luke warm...

sounding like a circulation problem, (blockage??) what with the pumps and so on, but how can prove that and any tips in finding the bloackage??

or is it totally some thing else..

cheers.
 
Sponsored Links
Sounds like a badly sludged system or a blocked pump impeller.

When previous pumps were changed the system should have been cleaned properly!

Tony
 
Sponsored Links
look in frequently asked questions , if your systems dirty it willcause the pump to fail eventually . Drain some water at a drain point & see how bad it is .Also check the isolation valves are fully open under the boiler on the ch pipes , ive had them shut more than once
 