Does this mean the boiler will struggle if temperature falls below -1C?However there's no harm installing, say, a 24kW boiler as it will heat the cylinder faster and provide for colder winter temperatures. The Ecotec 624 has a modulation range from 8.7 to 24KW, which means it be modulating for external temperatures between -1C and 13C, which is very good.
No. I take it I just take the size from the catalog 40 Delta t section, no need to oversize?Have the radiators been sized to take account of the 20C temperature differential required by the boiler?
True, but after the 406 litres in the first 10 minutes it sounded good to me. It's not so impressive now that I understand that it can only be achieved with a 48KW boiler!The ACV has some very impressive performance figures hence my picking it - 406 litres at 40C in the first 10 minutes, continuous flow at 40C of 1132litres/min(hr?)The hot water flow rate cannot be any faster than the incoming cold water flow rate! 1132 litres/hr = 18.32 l/min, which is nothing spectacular..
We had a lead supply pipe which was measured, can't remember the figures. But, it is being replaced with a 32mm mdpe which is awaiting connection by Thames Water. Plumber has said to me not to worry, flow and pressuure will be good and adequate for a pressurised system.Don't forget that, if you have an unvented HW cylinder, fed directly from the mains, all hot and cold water is supplied from the incoming mains, so using the washing machine may have an effect on the flow rate from the bath tap or the shower. It will all depend on the water pressure and the incoming cold water flow rate. Have these been measured?