Big_Spark
Beanzy, at the supply end you fit a 500mA 40A Type C time delayed RCD, this will protect the cable, and the installation involved.
At the garage end, the power to the Amps I would supply via a Type C MCB if the inrush currents are high, however in my experience this is not the case, so would settle for a Type B.
It would be wise to seperate the circuits though and have two or three 16 or 20A rated circuits.
I think people often forget that the Garage MUST be RCD protected, but that electronic equipment often results in nuisance tripping, hence the high fault current and time delay.
At the garage end, the power to the Amps I would supply via a Type C MCB if the inrush currents are high, however in my experience this is not the case, so would settle for a Type B.
It would be wise to seperate the circuits though and have two or three 16 or 20A rated circuits.
I think people often forget that the Garage MUST be RCD protected, but that electronic equipment often results in nuisance tripping, hence the high fault current and time delay.