Why I am sceptical of TT and RCDs
Caravan park toilet block. Supply to block on a 6mm 2 core SWA, from a TT source, 40amp fuse.
Inside this plastic box outside behind toilet block is just an RCD, then 6mm T&E into boiler room, to a straight 4 way board. Crap design, and poor workmanship.
6mm T&E has rodent damage, causing a good short to earth. RCD has failed. (Outside in extremes of temperature, probably never tested and rarely operated).
Fault current would of been around 50 or 60 amp as Zdb was around 3 or 4 ohm. While you would hope the fuse would eventually blow, it didn't. It just burnt away the 2.5mm earth connection lugged to the banjo with a blue eyelet, causing metalwork of installation to come live. Site maintenance received a shock while filling water system for the first time this season after winter drain down.
TT and RCDs can be nasty.
Caravan park toilet block. Supply to block on a 6mm 2 core SWA, from a TT source, 40amp fuse.
Inside this plastic box outside behind toilet block is just an RCD, then 6mm T&E into boiler room, to a straight 4 way board. Crap design, and poor workmanship.
6mm T&E has rodent damage, causing a good short to earth. RCD has failed. (Outside in extremes of temperature, probably never tested and rarely operated).
Fault current would of been around 50 or 60 amp as Zdb was around 3 or 4 ohm. While you would hope the fuse would eventually blow, it didn't. It just burnt away the 2.5mm earth connection lugged to the banjo with a blue eyelet, causing metalwork of installation to come live. Site maintenance received a shock while filling water system for the first time this season after winter drain down.
TT and RCDs can be nasty.