Yes, that would be my suspicion for what I suspect is another of those 'urban myths'.Being able to knock off all the MCBs and not expose the RCD to the IR test would be an explanation for the difference in perception.
Kind Regards, John.
Yes, that would be my suspicion for what I suspect is another of those 'urban myths'.Being able to knock off all the MCBs and not expose the RCD to the IR test would be an explanation for the difference in perception.
As I said, I've heard all this talk about RCBOs being 'more electronic', even though I didn't understand why, or eactly what the difference was meant to be. We're now being told that (as I suppose I suspected) this is not the case, so it would be quite interesting to ask manufacturers for the reason for the difference in 'IR testing warnings' to which you refer.RCBOs do have a warning label against IR testing them. RCCBs do not.
I have noticed that the tripping times of RCBOs are remarkably constant and similar. I had put this down to being 'less mechanical' (than RCCBs) because of what I have heard.
Look at section D in
http://www.mkelectric.com/Documents...uit Protection/RCBO's 43060PL Ed3.pdf[/QUOTE]
Thanks. That certainly seems to bust the myth pretty comprehensively...
NOTE: The following values of resistance will be encountered due
to the circuit of the RCBO alone, while performing insulation
resistance test using a 500V d.c. insulation test instrument.
Between L in or L out and > 100MΩ
N in or N out
Between L in or L out and > 100MΩ
Functional Earth
Between Neutral and Earth 2.7MΩ approx.
No mention of RCBO death there!
Kind Regards, John
EDIT - Sorry posted wrong link
Look at section H in
http://www.farnell.com/datasheets/97298.pdf[/QUOTE]
I'm confused - that one seems to say exactly the same as the one you previously posted (and I quoted from). Am I missing something?
Kind Regards, John.
I'm totally lost. Could you perhaps try to spoon feed me with what you are trying to say (in this and related posts)? Thanks.No I now take it to mean remove RCBO when testing the RCBO itself.
Indeed. It's having seen/heard everyone apparently believing that which led me to also assume that it had to be true! As I've said, I've never seen anything 'official' in writing which confirms such a belief.Yes, sorry about my edit. When I had another look the wrong bit came up. As to the discussion - When seeing the notice "remove the RCBO when insulation testing" (or words to that effect) I, and everyone else it seems, assumed it meant that the RCBO would be damaged.
Well, I'd certainly agree that the notice is very bad, since we are all struggling to understand what it means - and it's at least possible that nearly everyone has been misinterpreting it - a 'notice' could hardly fail its intended purpose more comprehensively than that! My problem with what you say above ('process to test the RCBO itself') is that I would not have thought that would be a process one would normally undertake - at least, not routinely. You don't do that with MCBs or RCDs do you, so why for an RCBO?Although it does say "When the installation has been completed", I take it to mean the opposite in that it would appear to be a process to test the RCBO itself which lf still connected to the installation would/may lead to false results for both. Would you agree?
Yes, I'm sure you're right - but, as I said, I don't think that IR testing of an isolated protection device (of any sort) is something one would nortmally do - unless out of interest, when one had already decided that it was faulty.Agreed. I just surmised that if the RCBO did not have these readings it may be faulty.
Yes, Of course, I've been slow in twigging that. Since the only problem IR measurement on a circuit with an RCBO connected is apparently the N-E one, the same can't possibly happen with an RCD, since it has no earth connection. I reckon that's wherein the myth was born!However, I can find no similar document relating to RCCBs so more likely a warning simply because of the earth wire on RCBOs and the relatively low N-E resistance,
Now that's an interesting difference I had forgotten - and I wonder why it is ?... the same can't possibly happen with an RCD, since it has no earth connection.