It seems that you probably have - or almost (see below)Wylex 240v, 50hz, 8A load, 100mA Trip, CAT.Wem 80/2 Current Operated Earth Leakage Circuit Breaker. Device must Switch off on testing if not seek advice ... Thanks John, because it doesn't say RCD I hadn't realized that that was what it was, but I see '100mA Trip, and 'Earth Leakage' so I think I had one without knowing?
Should that perhaps be "80A load" (rather than "8A load")?
Is that all it says? No mention of "time-delayed", "TD" or "Type S"? If it is not a time-delayed one, that is not ideal. It means that a fault causing the RCD in the CU to trip might well cause that external RCD to trip as well, thereby taking out all your circuits (including the lighting ones), not just those circuits protected by the CU's RCD - which rather cancels the benefit of having a 'split' CU (with not all circuits protected by the same RCD).
Kind Regards, John
Yes well spotted John it is 80A not 8A.
So the stand alone RCD is safe, but it would hinder diagnosis of what caused the trip.
No John, no mention of 'TD' or 'Type S' so it probably isn't time delayed. So presumably I need it removed or replaced, another job for Scottish Power or SWEB (South West Electricity Board)