Thanks Holmslaw. One last question, I am also fitting a mirror with demister pad and built in pullcord on/off function - could this come from the 3amp FCU or once again a separate one?
Never seen a demister, but assuming its 200 or 300 watts, treat it the same as the shaver point. What rating is it? in watts
It must be more than 8w. Have another look...
1.5mm² should cover it. Make sure it is no smaller than the existing lighting cable though.
A circuit breaker is not the same as an rcd.
And an rcbo combines the functions of a circuit breaker and an rcd.
Either, change the 5A breaker for a 5A 30mA rcbo,
Or, fit a 5A 30mA rcd in an enclosure beside the cu, and wire from the circuit breaker through the rcd and then to the bathroom.
Rcd's and rcbo's have to be tested to prove correct operation so you need to contact a spark with the correct test equipment.
I think you should contact a part p registered spark, this is less than a days work.
I'm concerned that you have'nt got your head round you're requirements.
eg. you now advise you have "10 x 12v Mini LED's in bath panel (0.1w total) - transformer fused plug".
If the only work you are carrying out is the replacement of the light fitting, I would recommend that you provide RCD protection for the lighting circuit. You would not, in my opinion, be required to provide RCD protection for other circuits within the bathroom, although this could be commented on in any certification provided.