Hi all, I wanted to replace my RWB2 with a horstmann s27r programmer.
I am reasonably clever when it come to diagrams but I can not figure this out at all!.
Currently on the RWB2 I have
On the back of the RWB2 it shows the internals like this
as per the direct replacement rwb29
http://w3.siemens.co.uk/buildingtec...-controls/documentation/Documents/rwb29_i.pdf
and the horstmann s27r shows the same set up
as per
http://www.horstmann.co.uk/downloads/ElectronicDocuments/Central-Heating/S21-I.pdf
So in my mind, it should jus tbe a straight swap?
But it does not turn anything on when installed.
I then read on and think I have a fully pumped y plan system and saw a post saying about a common problem with this deisgn that the CH can not be run on its own.
I always though the HW had to be on for CH to be on.
I am reasonably clever when it come to diagrams but I can not figure this out at all!.
Currently on the RWB2 I have
On the back of the RWB2 it shows the internals like this
as per the direct replacement rwb29
http://w3.siemens.co.uk/buildingtec...-controls/documentation/Documents/rwb29_i.pdf
and the horstmann s27r shows the same set up
as per
http://www.horstmann.co.uk/downloads/ElectronicDocuments/Central-Heating/S21-I.pdf
So in my mind, it should jus tbe a straight swap?
But it does not turn anything on when installed.
I then read on and think I have a fully pumped y plan system and saw a post saying about a common problem with this deisgn that the CH can not be run on its own.
I always though the HW had to be on for CH to be on.
This sounds like a y plan system.
A fairly common design fault with this system is that in order for it to work in heating only an extra signal is required to drive the valve into its third position.
The extra wire from the programmer is require to do this from the HW off terminal on the programmer.
However this is not required if the water has heated up when the valve should go to the heating only position.
This is only true however if the cylinder stat has been wired correctly to give the hw satisfied signal(they sometimes are not).
The cw output from the timer has to be on however for this to work even though the valve should only be open on the heating side.
Read more: //www.diynot.com/forums/viewtopic.php?p=1277794#1277794#ixzz2hMRNxje2[/QUOTE]
So 2 question really.
1. What wires do I need to change to get the new programmer to do its job (if any?).
2. Can i have just CH running for an hour without having the boiler on to heat the water?
(I understand this will just drain the heat from HW tank)[/url]