I would recommend fitting a double pole switch ( Live and Neutral ) so that the lamps when OFF are fully isolated.
If only the Live is switched then if a lamp develops a fault Neutral to Earth ( damaged or moisture in the lamp ) an RCD protecting the circuit may trip even though the lamps are switched OFF
Some appliances need 20 Amp switches
It is just as easy to manufacture a 20 Amp switch as it is to manufacture a 6 Amp DP switch ( the contact pads are just a bit larger ).
I presume that the confusion arises becasuse, although double-pole switches (usually at least 20A) are common, one would probably struggle to find any of them described as 'light switches'.
However, a double-pole switch is obviously a double-pole switch - and it doesn't know whether it is being used to switch a small lighting load or something much greater (like an immersion heater).