Yes, very stupid - I'll second that.This is getting stupid.... Can we just all accept that the arrangement which was suggested earlier is compliant with BS7671 but is rather poor, rather like the green/yellow core sleeved as live is, and move on?.... please!
It's an excellent analogy.
Why can't you answer my simple question? The ridiculous circuit you describe would comply with 433.3, but only in very specific situations, none of which exist in the average house.
Never disputed. Or schedule 4 in conjunction with whatever other parts of the building regulations of which it is a part may have an effect.1) We are discussing things ONLY in the context of Schedule 4.
2)The cable can't be separated from the "work which consists of adding a socket," since it's a necessary part of that work.
I would just add (as a 'final' comment!) that a major concern over the 32A MCB/2.5mm² cable/one socket design is that, even if arguably BS7671-complaint, someone, maybe a DIYer, could come across this circuit subsequently and 'innocently' add sockets (without seemingly needing notification), without realising that the CCC of the cable could thereby be exceeded.
That's a flaw in the regs. They might assume that the maximum current on the spur will be 20A, but we all know that there's nothing to stop somebody plugging two 13A loads into a double socket.And the assumed max current is 20A not 26A, where did you dream that up?
There would obviously always be a need for devices to provide fault protection, but you're probably right to question whether, in practice, overload protection actually achieves anything much, except in cases in which an installation is seriously abused.If your very incorect interpretation of 433.3 was correct we could do away with most protective devices.
Ok, so you haven't a clue what 433.3 means, the circuit it describes is ok in areas with no "fire risk", hence my analogy with the matches.
There is a specific reg applicable to rfc's (can't be bothered to look it up) that allows a 2.5mm unfused spur. And the assumed max current is 20A not 26A, where did you dream that up?
That does not mean you can by design install cables with lower ratings than the protective device in any situation.
If your very incorect interpretation of 433.3 was correct we could do away with most protective devices. And if you can't understand that, there is something seriously lacking in your ability to apply and interconnect the regs.