While a 2 amp socket will carry 12 amps the design of a 2 amp fixture on a circuit fused at 6 amps is not a good designas lighting circuits are already fused at 6 amps. All you need is a switch and flex outlet or else a 2 amp plug and socket.
12 amps is the current that can flow through a 6 amp MCB for quite a long time before the MCB's thermal trip will operate
Maybe so, but 2 amp sockets were always wired on to lighting circuits. They were deemed to require half an amp. There were never any 2 amp circuits, though I am aware that 2A MCBs are available.
If the OP is worried he could use a 5 amp socket, but in theory as 5amp sockets are deemed to require full load he could not put it on an existing lighting circuit with other lights.