So that appears to leave me up the creek as they say, I need to derate the fuse so that the derated current can never be exceeded, but the law will not allow lower value fuses? That sounds a little silly surely if the fuse is smaller it's safe?
It's the Wiring Regulations rather than an actual law, but there is an actual law requiring you to make reasonable provision in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury, and the accepted way of doing that is to comply with the Wiring Regs.
Ring finals are a special case of cables rated at less than the protective device and supplying accessories and appliances in parallel but not complying with any of the requirements that parallel cables otherwise must, and that special case only admits 30/32A devices.
If I was to consider up-grading the 4mm cable what do you think about jointing it in only at the studs where I want the insulation to go?
You could do that, but wouldn't it be less aggro to replace the cable entirely? Or replace it between the first/last sockets before/after it enters the wall?
Or would hidden cable joints be illegal?
Not if crimped.
So to clarify as far as I understand:
I cannot fit a 20A fuse on a final ring?
I need to derate my 2.5mm cable if it is run inside conduit next to sound insulation inside a stud wall?
4mm is the only compliant/safe way to run a final ring if the cable is run inside conduit next to sound insulation batts inside a stud wall?
No, yes and yes respectively.
But - how much of the circuit runs in the walls? All the way through horizontally, or up and down from the floor? How serious do you need the sound insulation to be? Obviously not very or you'd have to be doing a lot more than stick in some rockwool, so could you create insulation free channels for the cables without the extra sound leakage being a problem?