This applies only to the central heating, when the space set temperature is achieved.
The boiler will still maintain the heatstore temperature to the level set by the hot water stat as long as hot water is selected on the programmer, so it will effectively cycle in the DHW mode
The store will maintain temp but the divertor will not open to allow water to be pumped around the rads u necessarily.
Every thing else you say I agree with. However I followed the advice you are giving above for 2 years in my mothers house, I was pulling my hair out trying to control the house, I tried all sorts, starting with the lock shield valve on the hall radiator where the thermostat was, then tried a wireless thermostat which I could move around, to some extent that worked, however rather surprised at where it worked best, it was on a tea trolley just 3 foot from radiator at best, once it worked I realised it was down to the time taken for heat to reach thermostat from the radiator, and being close reduced the hysteresis, however the boiler was a modulating boiler, so it did not get the radiator that hot.At least one radiator in the room with the thermostat installed should not have a TRV fitted. Otherwise the TRV could prevent the room thermostat from working properly.
Mine is very poor in its location with two doors between the wall thermostat and hall radiator, and two doors and a stair case on the other side. this can't really happen with my house, there are 6 radiators all able to send heat to centre of the house where the wall thermostat is located, it really needs moving to the living room, but on my to do list. Leaving a door open or closed, will affect the wall thermostat, so even with the algorithms of the Nest learning thermostat it can't learn as always changing.Be very careful when selecting where to site the room thermostat. Get it wrong and you will regret installing it.
When you get it, if the wiring terminals look like this:
View attachment 180607
Then the wiring is:
Remove the wire link between boiler terminals 2 & 3
Boiler terminal 2 connects to L (thermostat terminal 4)
Boiler terminal 3 connects to 'Open' (thermostat terminal 2)
Boiler terminal 6 connects to 'N' (thermostat terminal 3)
As you have purchased a programmable thermostat, that includes both time and temperature control, the existing heating time control at the boiler will need to be set to have the central heating permanently 'on'. But don't panic, that will allow the new thermostat to take over control.