Worcester Greenstar junior - no CH

Joined
26 Oct 2013
Messages
134
Reaction score
1
Location
Essex
Country
United Kingdom
Combi boilers has packed up again. Hot water is absolutely fine, but no CH.

Am thinking it’s possibly the diverter valve, although I only changed that 4-5 years ago, and am pretty sure that last time it was the other way round with CH working fine but with no hot water.

When I call for hot water, the pilot light comes on and everything is good, but when I ramp the thermostat up, the pilot light doesn’t come on, but also no error messages or anything on the boiler, no blue flashing lights or anything.

what’s the likelihood of it being a diverter valve again? Do they not last very long?

If I disconnected the wire to it, then forced it to CH, would that be a good way to prove it’s the issue?

It’s a Worcester Greenstar Junior, and it’s currently it’s wired up to a nest thermostat with heat link
 
Sponsored Links
Your boiler doesnt have a pilot light.
I suspect you don't have a combi boiler boiler either.
We need more info.
Do you have a hot water cylinder?
 
If I disconnected the wire to it, then forced it to CH, would that be a good way to prove it’s the issue?
You can attempt to bridge out the Nest Heatlink, to rule that out as the problem.
With the power safely isolated, place the wire in terminal 3 of the (Gen3) Heatlink, into terminal 2, along with the wire that is already there.
If the heating comes on when the power is restored, blame the Heatlink.

If the Heatlink isn't gen3, or you don't understand the wiring, post a picture here.
 
Sponsored Links

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top