So, you are saying its generally cycling on and off on the boiler control stat setting (quite normal) but if you shut it down or its a programmed then you find the hi limit stat has locked out the boiler? What temperature is the boiler control stat set to?.
I have a 19 yeard old firebird (non combi) with boiler stat set to 75C which means it cycles on and off beytween 75C and~ 65C, if I measure the flow temp after it shuts down it rises to ~ 90/92C due to having no pump overrun but this has never been a problem as my (and most( hi limit stats are set to operate at 110C to 113C so a long away from this. Its a possibility if you have the control stat setting turned up fully.
Is it happening after just the CH is on or is it also happening after the DHW is on?
I have a 19 yeard old firebird (non combi) with boiler stat set to 75C which means it cycles on and off beytween 75C and~ 65C, if I measure the flow temp after it shuts down it rises to ~ 90/92C due to having no pump overrun but this has never been a problem as my (and most( hi limit stats are set to operate at 110C to 113C so a long away from this. Its a possibility if you have the control stat setting turned up fully.
Is it happening after just the CH is on or is it also happening after the DHW is on?