I think you have missed the point. The MCB protects the cable before changing an MCB you need to inspect and test to find out the current rating of the cable.
I have not worked on that type of board for some time and some boards will allow you to simply swap one MCB others you need to basic strip the board and rebuild as once the MCB is clipped in you can't reach the clip to release it without stripping board.
The DNO fuse can be 60, 80, or 100 and if 60 then a 63A RCD on all circuits is not a problem. If it's 100 then it could be. There is no simple answer.
However step one is the readings we expect 1.37Ω impedance with a 32A B type and 1.09Ω with a 40A B type to assume it was 1.37Ω because a 32A MCB is already fitted is one thing, but to cross your fingers and hope it is within the 1.09Ω is something else. The same applies to the route, to assume it is such that cable is good for 32A as already fitted with 32A is one thing, to cross your fingers and pray it's OK for 40A is clearly not the way to do things.
In my house when the cavity wall insulation was fitted I was very careful to insure the installers did not put it where I know cables are in the cavity. But likely most houses now have de-rated cables due to cavity wall and loft insulation. To swap a 32A for a 40A MCB is not as easy as undoing and tightening screws.
I have not worked on that type of board for some time and some boards will allow you to simply swap one MCB others you need to basic strip the board and rebuild as once the MCB is clipped in you can't reach the clip to release it without stripping board.
The DNO fuse can be 60, 80, or 100 and if 60 then a 63A RCD on all circuits is not a problem. If it's 100 then it could be. There is no simple answer.
However step one is the readings we expect 1.37Ω impedance with a 32A B type and 1.09Ω with a 40A B type to assume it was 1.37Ω because a 32A MCB is already fitted is one thing, but to cross your fingers and hope it is within the 1.09Ω is something else. The same applies to the route, to assume it is such that cable is good for 32A as already fitted with 32A is one thing, to cross your fingers and pray it's OK for 40A is clearly not the way to do things.
In my house when the cavity wall insulation was fitted I was very careful to insure the installers did not put it where I know cables are in the cavity. But likely most houses now have de-rated cables due to cavity wall and loft insulation. To swap a 32A for a 40A MCB is not as easy as undoing and tightening screws.