Is it only a requirement to zone if the house is over 150sqm in new builds now?
The use of the word "should" meaning that it is not a requirement but a recommendation?Assuming that you are referring to a wet heating system, that would seem to be in line with Part L of the building regs 2021.
5.14 For wet heating systems in new dwellings with a floor area of 150m2 or greater, a minimum of two independently controlled heating circuits should be provided.
5.15 System controls should be wired so that when there is no demand for space heating or hot water the heating appliance and pump are switched off.
Certainly should be, not only because that's the regulations but also because that's when they're at their most efficient. Condensing boilers became mandatory over 17 years ago, it's good to see the regs finally catching up with the technologyOk thanks. Also what about the new part L requirement.that radiators should be sized for a 55 degree flow temperature? Are people sizing rads for a 55 degree flow even though there installing them on a gas boiler installation?