Our level 3 lecturer seems to be confused on how to use the tables in appendix I, for calculating Zs.
They said that you look up the resistance in Table I1 and if the ambient temp is below 25°C, use the factors in Table I2. If over 25°c, use table I3.
I don't think this is right. Table I2 is a correction for temperature and table I3 is a correction for cable insulation type.
I think that table I2 is only used for testing not for doing Zs calcs when checking circuit protection design.
Any ideas?
Cheers!