Not sure what you mean.I would be interested to know what the difference between the 3 lead L-PE test is compared to the later models No Trip test.
There have always been (relatively) high current EFLI testers but with the coming of RCDs something was devised to test it without tripping the RCD.
That's just Fluke's way of doing it with the 1650 range - I don't know about others.
As above, I believe it does it really quickly - possibly a few times - rather than use such a low current which would not trip an RCD.
With the appropriate meter settings -
The two wire test is so-called high current (and considered more accurate but Fluke's no-trip is quite accurate compared to other makes?), which will trip the RCD, but as I said, if there is no RCD it can be used for EFLI by placing the Neutral lead on the circuit CPC.
The three wire test is automatically non-trip and, conversely, to test L-N loop where there is an RCD place the Neutral lead and Earth lead on the circuit Neutral.