My error - when I said "current" I meant "voltage" wrt potential difference across the terminals.
Which, thinking about it, still wouldn't tell me anything other than my mains voltage. I need a drink. ;-D
My error - when I said "current" I meant "voltage" wrt potential difference across the terminals.
Even if unintentional, what you sugegsted was not as silly as you suggest. As I recently wrote, IF you measured the pd between L-in and L-out of the MCB (I also said with neutral, but that would not apply to a single-pole MCB!!), if current is flowing through the MCB, you will see a very small pd due to that current flowing through the (very small) internal impedance of the MCB. As I said, it would be a very small voltage - but it should be 'measurable', and any pd between those terminals would mean that current was flowing through it.Which, thinking about it, still wouldn't tell me anything other than my mains voltage. I need a drink. ;-DMy error - when I said "current" I meant "voltage" wrt potential difference across the terminals.
Yes, as I said, a 'leakage' current great enough to produce the observed effects (probably well over 10A, presumably 'continuous') would almost have 'shown itself' - by smell, smoke, flames or whatever!Current drawn measured with a clamp meter is the next thing to check. I've had the insides of sockets etc. burnt out and tracking over causing MCBs to trip after a while. There is usually a burning smell with it though.
But no, it was all nipped up nice and tight. t.
True - but, if that were the case, to explain the OP's experience, the same error would have had to have been made when installing the replacement MCB - which still tripped.It might well be tight even if the busbar pring has missed the cage terminal. Het generated can be conducted into the MCB and operate the thermal element.
Most of those heaters run red hot if there is no forced air flow through the coils.Maybe this is the answer to all those house fires, it was not build up of fluff but shorted coils on the heater?
I would agree, however my point is likely it is the drier rather than installation. My energy meter has a max amps setting and run amps setting so it would be a simple test to plug it in. I would be happier using the clamp on in case the excess amps damaged my plug in energy meter, but the test is easy and the equipment is cheap, so I would likely watch it rather than walk away, but the red over current LED on the energy meter will soon show if a real over load or not even without reading what the digital display shows.Most of those heaters run red hot if there is no force air flow through the coils.Maybe this is the answer to all those house fires, it was not build up of fluff but shorted coils on the heater?
It could be the motor in the tumble drier has suffered wear and tear causing the in rush current when it starts / reverses to become higher and / or longer duration. This could happen if the motor is not able to reach normal speed as quickly as it did when new.
The dryer is only a month old so shouldn't be faulty.
Although that is all true, I don't think it could be an explanation for the MCB tripping after the dryer had been running for 20 mins.It could be the motor in the tumble drier has suffered wear and tear causing the in rush current when it starts / reverses to become higher and / or longer duration. This could happen if the motor is not able to reach normal speed as quickly as it did when new.