I suggested no such thing.Are we saying that there is no need to glue the conduit joins?
I suggested no such thing.Are we saying that there is no need to glue the conduit joins?
My hedge trimmer could probably get through plastic conduit without much difficulty (it has certainly been known to get through a garden hose ).I think there is merit in using conduit for mechanical protection. Over the years, I have seen a few cables chopped by hedgetrimmers etc...
Maybe - but the design of most hedge cutter blades is such that they would probably be fairly hard-pressed to damage a cable which was clipped firmly (at frequent intervals) direct to a wall, whereas the more protruding conduit (and contained cable) would probably be a more susceptible target! ... so maybe swings and roundabouts to some extent.But with something rigid like conduit ( as compared to a floppy hose [ooh err missus!]), the conduit may prevent damage to the cable by alerting the unalert user of said chopping device to the fact that it is no longer slicing through the shrubbery.
That couldn't possibly be prevented by PVC conduit. Steel conduit would be required to achieve that end (or for the end user to exercise a bit more care).I think there is merit in using conduit for mechanical protection.
Over the years, I have seen a few cables chopped by hedgetrimmers etc...
Oops sorry, i picked up the 16th, i will look later, its too do with all Non metallic conduit and fittings must be a certain bs number, which i quess will not the same as plumbing pipeCould you translate that into 17th ed-speak?
Kind Regards, John
Fair enough - I look forward to hearing what 17th ed refulation we are talking about.Oops sorry, i picked up the 16th, i will look later, its too do with all Non metallic conduit and fittings must be a certain bs number, which i quess will not the same as plumbing pipe
A normal coupler really isn't suitable for that purpose. That's why expansion couplers are manufactured.On the topic of 'to glue or not to glue', to me it's a case of glueing some joins and not others, so you're not just allowing for expansion, you're thinking about where it will happen and by how much.
For example, if I was putting up a PVC conduit run that went down 1.5m, then to the right 6m, I would install it like this... (saddles omitted!)
View attachment 140450
With the join on the right into the terminal box, if it was was a very hot day, I'd shove the tube all the way in. If it was cold, about half way in.
With a 6 metre run and allowing for a 30° temperature change throughout the year, it will expand/contract by 10.8mm. Seeing as the couplers and terminal boxes allow 20mm of tube entry, everything will be fine. I would never do a 9m run without a through box in the middle somewhere, just to cover the rare days when it's outside of my -5 to 25° 'estimate'.
The worst conduit jobs I've seen are when the PVC has shrunk too much and popped out of a join, then when it expands in the summer, that's when the trouble starts and it goes wavy and looks awful! Putting some thought into the installation solves all that.
Gaz
Most of what you say makes fairly good sense. However, I would point out that, even in the UK, a black object in direct sunlight can get very much hotter than 25°. Just this afternoon, the (black) wing mirror of my car (not to mention the steering wheel) were far too hot to touch - hence probably at least 50°-60°..... just to cover the rare days when it's outside of my -5 to 25° 'estimate'.
a black object in direct sunlight can get very much hotter than 25°
A normal coupler really isn't suitable for that purpose.