1.Have you had any work done around the time the fault started . Ie chance of a nail through a wire or drilling near a wire.
2. Were the zones valves changed because the contacts had become fused shut.
3. What is the voltage sat on the orange wire from WC when no call for Heat or HW.
4. Is this only effecting the pump , ie does the boiler fire at the same time as pump running constantly.
5. Have only the valve heads been changed ?
6. If the valve body is the same one throughout the fault , could this be sticking.
7. Has the circuit to the faulty valve been isolated and cables tested for continuity and insulation resistance.
Good morning
1. No work done at all - nothing.
2. The zone valves were changed as it was assumed they had 'sticky micro switches' - the last engineer actually looked inside the actuator and the micro switches weren't fused shut or 'fried'.
3. When the fault was present, there was 240v in the orange wire - no call for heat or HW - even changing the programmer /timer to off did not stop the pump from running.
4. The pump runs constantly and the boiler fires up too.
5. The whole actuators have been changed - including the brass valve on the pipes
6. The 'live feed' is always on the heating valve side - it only happens once the heating has been on. The room thermostat is satisfied, stops the demand for head, the valve shuts so the radiators cool down, but the pump keeps going circulating the water around the pipe work in the airing cupboard,firing the boiler up.
7. The cables were checked using a multimeter yesterday, but no stray voltage anywhere ?
Apologies if I'm not thorough enough in my details, make up and pretty clothes are my forte, so this is all new to me. But, I'm fast on my way to becoming a heating apprentice