Not thick.
You knew what you meant but we only knew what you wrote.
You knew what you meant but we only knew what you wrote.
Are you tunneling (approx. 12'250 km), or using the great circle (approx. 16'500 km), bearing in mind, you may need a diversion around Russia!?I`ll allow some approximation on the figures
Well, yes.So what is the conclusion? Are unfused appliances allowed or not and why the informative "no" to the first post?
Ok.Thanks EFL and note what I'm about to say will not apply to my installation as (already mentioned) I will be putting it on a fused spur and monitor it. If it blows said fuse I'll put it on a dedicated circuit. The below is more theoretical than anything else.
Well, sort of but if you have a 2.5mm² unfused spur then you should not have anything connected to it which could cause an overload.The bit of the on site guide I pasted in here, says "unfused" i.e. no plug top and no 13A fuse. So presumably it would in fact be ok to connect anything rated less than 32A on that circuit (making diversity allowances for the sockets and ensuring the cable is sized correctly which above 27 it might need more than 2.5mm). So something that might once peak at 25a for a very short period then drop well below 9A could be directly connected as an un-fused spur using 2.5mm could it not ?
1/ I suppose the word unlikely is to take into account yes overloads are allowed, preferably of short duration are allowed otherwise we would have fuses popping all over the place. Small overloads can be tolerated for a long time, large overloads to trip in the "conventional time" often 2 hours but could 4 hours sometimes. Medium overloads of very long duration is something best avoided by design. If we consider most circuits can be able carry 13% overload indefinitely but 45% overloads must trip (eventually) then we consider that somewhere between 13+% and 45-% might/might not trip can become a sobering thought.I see a few issues with what was proposed in the original post (disregarding for now that the appliance may not need 25A after all).
1. The dispensation that allows ring circuits with a cable smaller than the normal cable size for the breaker providing that overloading is merely "unlikely" (rather than not possible) is for circuits supplying accesories to BS1363. That means either sockets for fused plugs, or fused connection units.
2. While BS7671 doesn't require manufacturers instructions to be followed exactly, only to be "taken into consideration", if you ignore what the manufacturer says about fuse ratings and there is a problem then on your head be it.
3. You are using a large proportion of the circuits total capacity for a single load. Is that appropriate, remember overload protection is supposed to be overload protection not load limiting.
Who knows? - although it would be very useful at times, I unfortunately cannot read minds!Could it be that a 25A cct is a standard radial circuit where the manufacturers come from?
I suspect his 'point' (joke!) was that there would probably be quite an appreciable voltage drop in a cable running from the UK (ar any other country which used 'UK plugs') to AustraliaYes agreed but I`m unsure of the point you`re making here?