Electric Welders
An application for connection for welding purposes should state clearly the type, rating and supply voltage of the welding equipment before any arrangement is made for its installation. The connection of welding equipment is subject to the following factors that will be taken in to account on receipt of an Application form.
(a) Welders for connection between phase and neutral lines (nominally 230V) can be accepted for ratings only of 5kVA and below.
(b) Welders above 5kVA rating where the connection to the customer is not at high voltage should be connected
between phases of the three-phase supply (nominally 400V).
(c) Provision should be made for the correction of the power factor of the installation, which, because of the connection of welding equipment, may be unduly low The foregoing factors are applicable to most parts of Electricity North West’s electricity distribution network but there may be special cases where even these factors will be subject to modification.
(d) Welders, such as resistance types, having high ratings may require a supply delivered to the premises at high voltage and are the subject of special negotiations with Electricity North West for each individual case