Only a few amps through the neutral then, should be fine. Max would be 13ish amps with separately switched loads.
He said it is spread over the 3 phases in the opExcept I'm still not sure if the "3 circuits" mentioned in post #6 are on the same phase or not....
edit wrong post number
Who are "they", and why does this concern you?They have run L1 to one Element 230 volts L2 to second Element L3 to single phase motor All relying on the one neutrel in the 4 core SWA
523.6.3OK, so this just boils down to "how does the neutral work in a 3-phase system"? Answer, the current in the neutral is never greater than the current in the highest-current phase.
That's certainly true if the load is totally resistive. However, without doing some scribbling I wonder if that necessarily remains true when PF starts wandering - particularly if (as in the OP's case) each phase has a separate L-N load, with those three loads differing markedly in PF (two resistive and one inductive in the OP's case)??OK, so this just boils down to "how does the neutral work in a 3-phase system"? Answer, the current in the neutral is never greater than the current in the highest-current phase. Google will find some nice vector diagrams showing why, if you're curious.
Ok So The Current will never Be more then the largest load ie one of the 3 kw Element
Thanks
Indeed - but, more simply, as I've just written, could not the fact that L1-N and L2-N loads are both resistive, but L3-N highly inductive cause the neutral current to be higher than one would expect if all loads were resistive? (as I said, I need to do some scribbling, but maybe you can answer the question before I get there ).In most cases that is true. ... However it is possible, if electronic controls are involved to regulate the motor speed or element power, for strange harmonics and phase shifts to be introduced and cause a higher neutral current. Stage lighting dimmers are often fittet with an oversized neutral conductor for this reason.
Thanks - as I expected, and you got there before I got around to reaching for my 'scribbling pencil'True John, let's try to quantify it... So you might have 50% more current in the neutral than you would expect.