3 phase testing

supersparks said:
join together all phases and test between them and neutral.

then test between phases.

or you can test between each of the live conductors in turn.

thats not what you said earlier...
supersparks said:
or you can just link out the 3 phases and test to earth and neutral, and between earth and neutral
 
Sponsored Links
In order to terst properly and record the result you need to test the individual phases between each other and Neutral and Earth...anything short of that may be adequate as it would show any shortcomings, but it is not the accepted method for the recording of those results.

For a quick test to ensure there was no fault on a circuit you have problems with..it would be ok, but not for commissioning testing or even a true PIR.
 
You can do an insulation resistance test on a 3phase distribution on purely the tales
L1+L2
L1L2+L3
L1L2L3+N
L1L2L3N+CPC

Testing of course in 'M' ohms.

but if the reading is low i.e. less than <99.99 M Ohms

Then each circuit should be tested individually using the Insulation Resistance test

Thanks in advance guys
 
Sponsored Links
basic said:
You can do an insulation resistance test on a 3phase distribution on purely the tales

Only as a basic quick test, this would not be sufficient for commissioning or PIR purposes.
 
the electrican said:
what you did was fine but you need to test between l1,l2,l3,n to earth :D

incase your not aware, CPC is the technical term for earth, which he did mention to test between
basic said:
L1L2L3N+CPC
 