Ah, that makes sense then. As you probably realised, I was thinking about 0.4 (or 0.2) sec disconnection time. As you go on to say ...I’m using an example of a 60A submain so a 5 second disconnection time.
Indeed, as you imply, with a breaker the Zs will be the same for 0.4 and 5 seconds (since both require magnetic tripping), but with a fuse the Zs can be much higher for 5 seconds. It's an interesting point, and not something I've really had to think about very much. The only significant submains I've had to deal with are those in my house and, being a TT installation, they get their fault protection from TD RCDs.The difference is explained when you look at the fuse graphs, as the operating current for a fuse is linear, and a circuit breaker is not as you need to operate the magnetic part of the circuit breaker to achieve the required disconnection time.
Kind Regards, John