By first glances, you do seem to have a 3 phase supply, however you appear to only have 2 phases in use.
left to right - 1= neutral/earth, 2= brown phase, 3= black phase, 4=grey phase (not in use)
You would need to check if it is true 3 phase supply, if so, you would need the grey phase checking for a fuse, then it will need connecting to the meter and a tail back out, then a suitable 3 phase isolator to then supply your 4 or 5 core swa to the garage
1st prize goes to Yorksparks.. Not true 3ph coming in after a lot of chasing to get it checked... 2x 1ph and one doubled up on the same phase.! Anyone want to buy a 3ph compressor..
It's been very informative and I have learnt a lot, a big THANKS to everyone who has taken the time to reply, all good advice too..